Definition of Electrical Vault vs Electrical room
gt40
New member
110.31 A defines the fire resistivity of Electrical Vaults - what constitutes a vault vs an electrical Room - The only Vault Definition is in 450 III for Transformer Vaults - are there any other definitions of vault in the NEC?
charlie b
Lockport, IL
Semi-Retired Electrical Engineer
Re: Definition of Electrical Vault vs Electrical room
I don?t think so. The NEC?s Article 100 definitions do not include the term ?vault,? nor does the NEC make a clear distinction between an ?electric room? and a ?vault.? It does state several circumstances in which certain equipment must be in a vault that meets the construction requirements of 450 Part III. But even 450 Part III does not include a definition of ?vault.?
tom baker
Bremerton, Washington
Master Electrician
I recall that the 1999 added rules for underground vaults I don't have my NEC, but the rules came from a ANSI standard. these are vaults for personell entry.
websparky
Cleveland, Ohio
Hi Guys,
If a "room" meets these specifications, it's a "vault".
2002 NEC 450.42 Walls, Roofs, and Floors.
The walls and roofs of vaults shall be constructed of materials that have adequate structural strength for the conditions with a minimum fire resistance of 3 hours. The floors of vaults in contact with the earth shall be of concrete that is not less than 100 mm (4 in.) thick, but where the vault is constructed with a vacant space or other stories below it, the floor shall have adequate structural strength for the load imposed thereon and a minimum fire resistance of 3 hours. For the purposes of this section, studs and wallboard construction shall not be acceptable.
charlie b
Lockport, IL
Originally posted by websparky:If a "room" meets these specifications, it's a "vault".
I don?t think this set of specifications constitutes a definition of ?vault.? I think the logic flows in the opposite direction. If you need to have a vault (450.21(C) is one article that requires one), then the article you quoted tells us how to build one. However, I can build a room that meets those specifications, and use it as a wine cellar, and it will not be, by definition, a ?vault.?
I know I?m being a nit-picker here. But a ?nit? is the egg of a louse, and who wants lice to grow to adulthood? The basic problem that I have with the NEC is the absence of the distinction that I mention in my first post above.
websparky
Cleveland, Ohio
Charlie,
I can see your point.
As we both know, the NEC is not an instruction manual nor is it THE answer to every question.
If it were, the amount of posts on all of the forums would likely be far less.
However, there are usually guidelines that we can ferret out and learn something from, just like in these forums.
Often times many members are looking for exact code references. Other times, they are simply asking for help in understanding. If we as fellow experienced electricians do not offer our opinions and guidance, we are doing a disservice to ourselves and those that are doing the asking.
Personally, I would rather give some advice or opinion that could help, rather than just saying the code does not answer the question and then comment on the inadequateness of the code.
The requirements listed in the code does describe a vault. However, you could build a wine celler to the same specs. But then, the subject was "vaults"!
charlie b
Lockport, IL
Originally posted by websparky:Personally, I would rather give some advice or opinion that could help, rather than just saying the code does not answer the question and then comment on the inadequateness of the code.
Then please allow me to state my opinion: I believe we should put the word ?vault? on our list of ?words we know but do not use often.? During conversations among friends, the term has been loosely applied to any room with a heavy door or any box-shaped space that is buried under dirt. But when we are bidding, designing, building, or inspecting, we should be careful to avoid ?Conversational English.? We should say ?vault? only when the technical requirements of the project explicitly demand the use of that word. And we should acknowledge that this type of project is rare.
The problem that I wish us all to avoid, would arise from that notion that if there is a transformer (or at least a big transformer) in a room, that room must necessarily be a ?vault,? and it must therefore conform to 450.21(C). This is not true.