I picked up a couple of MH's books as a Christmas present to myself. I am studying the Grounding Versus Bonding book and it is going over the definitions found in 250.2. I noticed that the definition of ground fault
An unintentional, electrically conducting connection between an ungrounded conductor of an electrical circuit and the normally non-current-carrying conductors , metallic enclosures, metallic raceways, metallic equipment or earth.
My question is this if the neutral conductor were to come into contact with normally non-current-carrying parts would this also be considered a ground fault condition? Wouldn't this cause objectionable current flow on these parts?
Joe