shelco

Senior Member
Inspector rejected a new resi service.
Meter base is mounted on the side of the house that the drive way is and he said that is falls under 230.50. We have a steel mast and the service cable to the panel comes out of the bottom for about one foot exposed. I think that this is a streach to consider this subject to damage. If it were a commercial area where you have delivery trucks in and out all day I would tend to agree but a residential drive way??. Any solid definition of subject to damage

Shelco
 

bphgravity

Senior Member
Location
Florida
Re: definition of subject to damage

Common sense usually prevails, but somtimes the issue from your perspective will be different than someone elses, including the inspectors. The best thing to do in these situations is to find out if there is anything you can do to protect or alter the equipment in place, at its current location. That way you at least don't have to relocate the whole installation.
 

charlie tuna

Senior Member
Location
Florida
Re: definition of subject to damage

ten foot of three inch conduit cut in half and secured in the ground by ten bags of concrete--build a ballard to protect the installation from vehicles-------------- but the inspector has the final say as to what is subject to damage--it can happen--can't it?
 

benaround

Senior Member
Location
Arizona
Re: definition of subject to damage

Shelco,

I've heard of this more than a few times,I think the concern is someone hitting the meter with a car or truck.

frank
 

charlie

Senior Member
Location
Indianapolis
Re: definition of subject to damage

The thing I don't understand is that we will require our cash register to be protected if we feel like it is likely to be damaged. Why is the inspector doing our job? :confused:
 

redfish

Senior Member
Re: definition of subject to damage

The thing I don't understand is that we will require our cash register to be protected if we feel like it is likely to be damaged. Why is the inspector doing our job? </font>
  • <font size="2" face="Verdana, Helvetica, sans-serif">Perhaps the AHJ is concerned that an injury or fatality could result if someone accidently damaged your cash register. :D</font>
<font size="2" face="Verdana, Helvetica, sans-serif">
 

jwelectric

Senior Member
Location
North Carolina
Re: definition of subject to damage

Originally posted by redfish:
The thing I don't understand is that we will require our cash register to be protected if we feel like it is likely to be damaged. Why is the inspector doing our job? </font>
  • <font size="2" face="Verdana, Helvetica, sans-serif">Perhaps the AHJ is concerned that an injury or fatality could result if someone accidently damaged your cash register. :D</font>
<font size="2" face="Verdana, Helvetica, sans-serif">
WHAT! Charlie is to kind hearted to hurt anyone, I Think :confused:
 

volt102

Senior Member
Location
New Hampshire
Re: definition of subject to damage

Look at the code article the inspector quoted (230.50). He/She is not conserned with the cash register being protected, 110.26(F)(2) does that. The inspector just wants the cable to be protected w/ rigid metal conduit, intermediate metal conduit, schedule 80 rigid nonmetallic conduit, electrical metallic tubing, or other approved means.
 

paul

Senior Member
Location
Snohomish, WA
Re: definition of subject to damage

Originally posted by volt102:
Look at the code article the inspector quoted (230.50). He/She is not conserned with the cash register being protected, 110.26(F)(2) does that. The inspector just wants the cable to be protected w/ rigid metal conduit, intermediate metal conduit, schedule 80 rigid nonmetallic conduit, electrical metallic tubing, or other approved means.
Yep, that's what I was thinking. If you put the cable in an LB or some sort of raceway, it should be good to go. As of now it's exposed. SE cable is all Greek to me, anyway. They don't allow the stuff out here.
 

stud696981

Senior Member
Re: definition of subject to damage

Maybe I'm mistaken, but it sounds like this was a new residence. If so, wasn't there plans and wasn't this specified on there.

If plans were submitted and approved for a permit the inspector is probably out of luck.

Around here unless there is an actual violation and NOT something subject to "his interpretation" like this, the inspector is stuck passing this since it was on the plans and his office approved them.
 

allenwayne

Senior Member
Re: definition of subject to damage

If plans were submitted and approved for a permit the inspector is probably out of luck.

Around here unless there is an actual violation and NOT something subject to "his interpretation" like this, the inspector is stuck passing this since it was on the plans and his office approved them.

To me that has always been a pet peeve !!!
We submit plans for approval,electrical inspector #1 inspects said plan #2 approves said plan #3 We have to explain to customer, builder,GC that the recessed can in a 24 in deep closet can`t go there because of clearance to shelf :roll:
 

shelco

Senior Member
Re: definition of subject to damage

This is not a new residence. It was an upgrade to an old service. The original location could not be use because of obstructions that have risen over the years so it was move to the only acceptable spot,driveway side of house. It really isn't that big a deal I am just going to put a bollard there even though you would have to go out of your way to hit it.
Thanks for the input.
Shelco
 

be4jc

Member
Re: definition of subject to damage

So what your saying is if the plan checker misses something that makes it OK!!!
Thats the craziest thing I've ever heard :eek:
 