Does anyone know if the ampacity of DEL or DLO (Diesel Electric cable) is given in the NEC?
D dennis5150 Member Jul 21, 2009 #1 Does anyone know if the ampacity of DEL or DLO (Diesel Electric cable) is given in the NEC?
iwire Moderator Staff member Location Massachusetts Jul 21, 2009 #2 dennis5150 said: Does anyone know if the ampacity of DEL or DLO (Diesel Electric cable) is given in the NEC? Click to expand... First it would have to be a cable type listed in Article 400, if it is then you can find the ampacity in Article 400.
B benaround Senior Member Location Arizona Jul 21, 2009 #3 dennis5150 said: Does anyone know if the ampacity of DEL or DLO (Diesel Electric cable) is given in the NEC? Click to expand... dennis, some DLO cable is dual rated RHW and RHW can be found in the NEC. note: 90degC terminations are generally required.
ron Senior Member Location New York, 40.7514,-73.9925 Jul 21, 2009 #4 Similar to Frank, I specify the DLO that has a dual listing with RHW2 which is found in the NEC. Use the ampacity found in the standard size lower than the DLO size you will be using in the regular table.