1. 250.66 and the Table
2. Delete all the text, add new text in 250.66, delete 250.66(B).
3. Delete Table 250.66 and reword 250.66 to state, "The size of the grounding electrode conductor of a grounded or ungrounded ac system shall not be less than 4 AWG copper wire or 2 AWG aluminum wire, except as permitted in 250.66(A).
4. Instead of me providing substantiation for the change, how about the CMP provide me substantiation for requiring a GEC larger than #4 copper for any application?
I have two structures both served with 600 kcmil service entrances. One has a underground metal water pipe, the other has no present electrodes. The first structure requires a 2/0 GEC the second only requires a ground rod or two and #6 AWG GEC. Both are compliant to the MINIMUM requirement of the NEC and will both ne as effective for whatever purpose the grounding electrode system supposedly accomplishes.
If a concrete encased electrode is considered to be the most effective and low-impedance electrode of choice, than why is it only required to be connected with #4 while other possibly less effective electrodes require such large conductors?
The code is suppose to be a minimum standard and exceeding what is proven to be an acceptable minimum installation is a design consideration and should not be in the NEC.
2. Delete all the text, add new text in 250.66, delete 250.66(B).
3. Delete Table 250.66 and reword 250.66 to state, "The size of the grounding electrode conductor of a grounded or ungrounded ac system shall not be less than 4 AWG copper wire or 2 AWG aluminum wire, except as permitted in 250.66(A).
4. Instead of me providing substantiation for the change, how about the CMP provide me substantiation for requiring a GEC larger than #4 copper for any application?
I have two structures both served with 600 kcmil service entrances. One has a underground metal water pipe, the other has no present electrodes. The first structure requires a 2/0 GEC the second only requires a ground rod or two and #6 AWG GEC. Both are compliant to the MINIMUM requirement of the NEC and will both ne as effective for whatever purpose the grounding electrode system supposedly accomplishes.
If a concrete encased electrode is considered to be the most effective and low-impedance electrode of choice, than why is it only required to be connected with #4 while other possibly less effective electrodes require such large conductors?
The code is suppose to be a minimum standard and exceeding what is proven to be an acceptable minimum installation is a design consideration and should not be in the NEC.