delta breaker

Status
Not open for further replies.

augie47

Moderator
Staff member
Location
Tennessee
Occupation
State Electrical Inspector (Retired)
as recall, it was a hybrid "two pole" breaker (to legs connected to the buss) with a third pole added that was supplied by a conductor (somewhat like a GFCI neutral conductor).
This allowed the breaker to be used in single phase panel with the 3rd phase connected directly to the breaker.
At one time they were common in small commercial buildings with limited 3 phase loads such as a "Mom and Pop" grocery with one three phase cooler.
(I believe some had a "Line" lug rather than a conductor)
 
Last edited:

infinity

Moderator
Staff member
Location
New Jersey
Occupation
Journeyman Electrician
as recall, it was a hybrid "two pole" breaker (to legs connected to the buss) with a third pole added that was supplied by a conductor (somewhat like a GFCI neutral conductor).
This allowed the breaker to be used in single phase panel with the 3rd phase connected directly to the breaker.
At one time they were common in small commercial buildings with limited 3 phase loads such as a "Mom and Pop" grocery with one three phase cooler.
(I believe some had a "Line" lug rather than a conductor)

How would you get the 3rd phase into the single phase panel?
 

augie47

Moderator
Staff member
Location
Tennessee
Occupation
State Electrical Inspector (Retired)
I have only seen two such installs (hard to believe I didn't install one)..
Both were "service" panels and the third phase was brought from the meter straight to the only "delta" breaker in the panel.
One of the many reasons they were later deemed "unsafe"
 

Wagbag

Member
Wagbag

Wagbag

Your question is interesting. Let me direct you to a 'must have' text book if you are an electrician, it is the Amerian Electricians' handbook by Terril Croft and Wilford Summers. Delta breakers/panels are still in service today and are unique and wonderful equipment. If you are unaware of how they work and you need to have maintenance performed on a panel, call up an electrical contractor and have them take care of it for you. I presume your life is of value to you and calling a qualifed electrician might just save it.
 

roger

Moderator
Staff member
Location
Fl
Occupation
Retired Electrician
Delta breakers/panels are still in service today and are unique and wonderful equipment.
A panel being serviced by a Delta is not part of this disscussion and IMO there nothing wonderful about a delta breaker. I installed three in the seventies, two were replacements and one was because the facility had one available and it suited their need.


Roger
 

norcal

Senior Member
Since the breaker in the link above is mine, I'll post some of the photos. :D

delta7.jpg



delta3.jpg



delta6.jpg


It was in the 1978 NEC 384-16(e) that prohibited delta breakers.
 

hurk27

Senior Member
The only time I have ever replaced one was at a plant I worked at that had a high leg delta service and had several single phase panels fed from "A", "C" legs to serve the 120/240 volt loads, and a couple of them had one of these installed to provide 3-phase for office air units, but that was back in "79 or 80"
 