Delta Breakers

Status
Not open for further replies.

Bowhunter

Member
Location
Illinois
Article 408.36 (C) addresses Delta Breakers and says they can't be used in panelboards. What are they? Where can I find information on them?
 

jim dungar

Moderator
Staff member
Location
Wisconsin
Occupation
PE (Retired) - Power Systems
Delta breakers have not been manufacturer for more than 30yrs (since the NEC prohibited them). They looked similar to a 2P GFCI except with lugs instead of a pigtail. Two poles plugged on to the panel bussing and the third phase was cabled direct to the breaker.

I know someone on this forum has a picture of one.
 