:thumbsup:Physically speaking, yes, they're in series, but not in the usual sense of the usage of the term.
In theory, one could open any corner of a delta secondary and there will be no voltage across the opening. In theory.
But going back to what OP said delta secondary is basically a closed loop. This is something I never thought of before - what prevents a circulating current from developing in that loop. Something tells me there can be some circulating current in that loop as a result of minor differences between each segment of the loop.180406-1440 EDT
Something else to consider:
Suppose I put a load on one secondary, could be a resistance. Now I have a series parallel circuit.
But for analysis purposes I can determine a series equivalent circuit for that one secondary and its load that consists of a voltage source of some voltage and phase angle, and a series equivalent internal impedance. If this equivalent circuit replaces the original secondary, then for analysis purposes I am back to the delta being a series circuit.
One definition of a series circuit says that a single current flows thru all elements of the circuit.
Thanks. I kind of was thinking sum of voltages - if perfect all cancels out and there is no current. Reality told me there is almost always some imperfections and that there would be at least some circulating currents most of the time.180407-1259 EDT
kwired:
Circulating currents do exist. The amount is determined by the sum of the voltages divided by the sum of the impedances. Harmonics become a very important consideration.
Any circulating current would have to result from an imbalance on the primary side. If the primary source is a delta bank it will be close to balanced, barring voltage drop from heavily unbalanced loads.Thanks. I kind of was thinking sum of voltages - if perfect all cancels out and there is no current. Reality told me there is almost always some imperfections and that there would be at least some circulating currents most of the time.