highpowered
- los angeles
I had a call on a overheating panel on this system. I have never seen this system in use before and dont know much about it. Has anyone worked with this before? Any suggestions on troubleshooting?
Yes went there 12am. The voltage to ground on the system is 110/208/110 3 wire.
Re-reading your OP it sounds like your are talking about (2) current transformers that may have been part of a metering circuit.
Are you saying these CTs failed, and then were bypassed? By who? How is the metering being done now?
Have you talked to the utility about this install?
There is no special consideration needed for grounding this type of service.
yes the CTs failed burned up completely. There are numerouse wiring problems with the subpanel that is connected to this meter.
1) using 3/0 in seperate 3/4 to 1" conduits per conductor.
2) since there is no nuetral on this 3 wire system they grabed a nuetral from the seperate single phase panel in the same building and ran it to the sub for the 3 phase 3 wire.
numerous bolt on clamps patching the wires.
3) the sub panel thats loading off the 3phase is operating at 150amps per leg 16hrs a day sometimes 24 hrs. at this rate the ampacity should be jumped up to at least 125%if not 300%. (I was thinking run parrallel 3/0 to fix this)
4) I dought that the conduits are bonded to said subpanel.
as far as the utility owner does not want permit so I cant upgrade the power to 400 amp or even 250 but I can replace failed parts with new ones without permit. The owners "electrician" did the work on this to bypass CTs. Looks like he ran sub-panel as well. By all means if I had alot of work right now id tell him to take a hike he is to cheap for me to fix this but I gotta pay the bills
If these were utility CTs why are they feeding a subpanel?
Do you have a Service Entrance panel that is 240/120V 3-phase 4-wire with a proper neutral (even if it is neutral only between two lines)?
Is your problem panel a 3-phase 3-wire branch circuit panel fed by the service panel?
Single conductors run in individual metallic conduits are likely to overheat.
The nuetral they took is from a seperate service drop in a seperate electrical system in the same structure single phase.
Sounds like a disaster in the making.
Keep in mind, IF you do work on it without permits/inspections and it eventually fails, which seems likely from what you say, the one thing the owner, his lawyer and your local enforcement will remember is that YOU "are their electrician".
The dollar you make today on this type job may cost your 10 X that in the future.
If you do nothing else, you should get rid of this 'neutral'.
If the service was really only 3-wire, it is possible it could have been metered using only 2-CT's.
Go fishing. This sounds like a mess.