Hello all,
I just realized that a Contractor installed a step up transformer 208V Delta to 480V delta. He brings grounds in from the primary feeder and sends ground out with the secondary feeder to an MCC (feeds several motor loads, plus some drives, plus some heating loads).
However, the transformer is not corner grounded, nor is it center tapped. This leaves it being ungrounded. Is it required to be grounded? In that case I assume making it a corner ground system would be easiest?
If it can be ungrounded, I assume a ground fault detector would need to be installed, plus some labeling be installed on the MCC, and then make sure no drives require the MOVs to be disconnected as a result of being connected to an ungrounded system.
Am I missing anything?