So I searched and searched and can't find any solid leads on this question. So hopefully someone can help me out.
I have a Delta - Delta Transformer rated at 45KVA. 480V -> 240V
The service I have a 3 Phase 277/480V.
I am assuming the output of the transformer is called the secondary.
I get 240V so everything is fine, I suppose.
I just don't know how much load or current I can run safely. Most calculators I see are Delta - Wye or Wye-Wye.
I am running computer servers and wanted to add more of them but don't want to do something stupid.
There is currently 16 servers that is consuming 1,800 watts each or 7.5A @ 240V. Just wanted to know if I could safely add 4 more computers of the same load.
I tried uploading the plate picture but it downsizes it to 12kb.
Thanks in advance!!