Delta- Delta transformer

Status
Not open for further replies.

EL Schulte

Member
Location
St Louis
I have a 480v pri 240v sec Delta-Delta transformer. I'm questioning how to bond it. The transformer diagram has nothing on Grounding the B phase (x2). But I'm 90% sure that is what I need to do. Before I do this I want to be 100% sure. Any help would be grateful
 

EL Schulte

Member
Location
St Louis
I have a 480v pri 240v sec Delta-Delta transformer. I'm questioning how to bond it. The transformer diagram has nothing on Grounding the B phase (x2). But I'm 90% sure that is what I need to do. Before I do this I want to be 100% sure. Any help would be grateful

Will the transformer Name plate have a Grounded B phase secondary diagram on it if it is capable of being grounded?
 

ActionDave

Chief Moderator
Staff member
Location
Durango, CO, 10 h 20 min from the winged horses.
Occupation
Licensed Electrician
I only have been around one corner grounded system, but as far as what the NEC says you pick one phase and ground it, B phase is customary but I don't think it's required. After that treat the grounded phase just like a neutral and follow 250.30 and 200.
 

Jraef

Moderator, OTD
Staff member
Location
San Francisco Bay Area, CA, USA
Occupation
Electrical Engineer
You don't actually HAVE TO ground one phase, you DO have to do that OR you must add ground fault monitoring and protection to the secondary side; one or the other. So the transformer nameplate diagram is not likely to show that, it's an installation decision on your part. It's a lot less expensive however to just use a corner grounded secondary and yes, B phase is the conventionally accepted one to ground, but it's not dictated.
 

EL Schulte

Member
Location
St Louis
Thank you this helps. One more question. This transformer will be supplying a panel for 3 phase 240v equipment only. I can use 3 pole breakers right.
 

kwired

Electron manager
Location
NE Nebraska
Occupation
EC
Thank you this helps. One more question. This transformer will be supplying a panel for 3 phase 240v equipment only. I can use 3 pole breakers right.
As long as the breakers are 240 volt and not 120/240 volt rated, but most 3 pole are not rated 120/240 AFAIK.

The transformer will not care which leg you ground, as long as there is only one leg grounded, more then one leg grounded is short circuit.

Make sure panel is rated for grounded phase system as well though. If so it may say "B" must be the grounded phase.
 

bob52

Member
Location
pittsfield ma
Delta - Delta transformer

Delta - Delta transformer

Once you ground one of the Phases ( corner grounding ) you can no longer use 3 pole breakers , as you cant have ocp on a grounded conductor
 

GoldDigger

Moderator
Staff member
Location
Placerville, CA, USA
Occupation
Retired PV System Designer
Once you ground one of the Phases ( corner grounding ) you can no longer use 3 pole breakers , as you cant have ocp on a grounded conductor
You can have OCP on a grounded conductor as long as it has a common trip with the ungrounded conductor(s).
That option is generally not available with fuses.

Sent from my XT1585 using Tapatalk
 

petersonra

Senior Member
Location
Northern illinois
Occupation
engineer
You can either ground it or not. It is a design decision. There are ramifications both ways.

personally, I doubt it makes all that much difference one way or the other, although I have to say grounded 3 phase systems seem to be more common these days than they once were.
 

Jraef

Moderator, OTD
Staff member
Location
San Francisco Bay Area, CA, USA
Occupation
Electrical Engineer
When I worked at a steel mill in the late 70s we were 480V ungrounded delta, because the attitude was "Damn the torpedoes, full speed ahead!" when it came to operating that plant. We had ground lights in the electric shop that told us if there was a ground fault, somewhere. Then we jumped in golf carts to go out and try to find it. The usual sign was a production manager running around like a chicken with it's head cut off, flagging us down because his part of the plant was down and he was going to miss quota and thus, his bonus.
 