Delta delta transformer
Jpflex
Electrician big leagues
Victorville
Electrician commercial and residential
My boss has a 300 KVA delta delta pad mounted 3 phase transformer with 4800 volts primary and 480 volts secondary
When trying to size primary and secondary wire I used formula:
KVA divided by primary voltage x 1.732 for primary conductors
And
KVA divided by secondary voltage x 1.742
Therefore before derating factors or multiplying by 1.25 percent for continuous loads I got
Primary current at 36.08 amperes
Secondary current 360.85 amperes
My boss says local utility and google told him secondary current was 669 amperes and to use a # 4 aluminum conductor for primary
Which is correct?
And are you supposed to mark up conductor ampacity to 1.25 percent full load current value for continuous loads for commercial use?
Thanks
And
KVA divided by secondary voltage x 1.742 Actually 1.732 also (typo)
Primary current at 36.08 amperes Yes
Secondary current 360.85 amperes Yes
My boss says local utility and google told him secondary current was 669 amperes No
and to use a # 4 aluminum conductor for primary You would select your OCP 450.3(A) and size your conductor to match the OCP device
Which is correct?
Thanks
Boss tried to say my figures were wrong because it’s pad mounted and commercial as if mounting style makes a difference