The electron man
Senior Member
- Location
- Nyc
- Occupation
- Electrician
So I was wondering if you had a delta delta transformer and one of the phase hit ground how would the current return to the source to trip the ocpd since you have no neutral ??
Thus the need for a grounded secondary point (neutral or corner) or ground-fault detection.So I was wondering if you had a delta delta transformer and one of the phase hit ground how would the current return to the source to trip the ocpd since you have no neutral ??
Translation, if I may:It waited for the second to hit it.
Thank you.Translation, if I may:
With an ungrounded system, the first unintentional ground fault would effectively make the system behave as an intentionally-grounded system, but with uncertain voltages.
Undetected, the system would likely continue to function until another ground fault occurred on a different system conductor, in which case OCPD should function as intended.
As she should be.I intended to get back, but MDSW is higher on the list.
It won't. It's like taking a battery and connecting just one terminal to ground. Nothing happens. But if the other terminal also connects to ground, THEN current flows, and a lot of it.So I was wondering if you had a delta delta transformer and one of the phase hit ground how would the current return to the source to trip the ocpd since you have no neutral ??
But a delta wye transformer would since its connected to the main service with a main bonding jumper that competes the circuit ??One clarification: The presence or lack of a neutral isn't the key point here. It is the presence or lack of an intentionally grounded terminal that makes the difference.
In theory you can ground _any_ terminal of a transformer to create a grounded system; with a delta secondary you can create a corner grounded system or perhaps a 'high leg' system. Similarly, if you have a wye secondary you could leave all the terminals ungrounded and have an ungrounded system.
Code has some specific requirements; if you use the neutral as a circuit conductor it _must_ be the grounded conductor. So if you have a wye secondary and you are using the neutral you can't legally install this as an ungrounded system.
-Jonathan
Only if/because there is a secondary system line, usually the neutral, that we "always" intentionally ground.But a delta wye transformer would since its connected to the main service with a main bonding jumper that competes the circuit ??
But a delta wye transformer would since its connected to the main service with a main bonding jumper that competes the circuit ??