So I was wondering if you had a delta delta transformer and one of the phase hit ground how would the current return to the source to trip the ocpd since you have no neutral ??
 
It waited for the second to hit it.
Translation, if I may:

With an ungrounded system, the first unintentional ground fault would effectively make the system behave as an intentionally-grounded system, but with uncertain voltages.

Undetected, the system would likely continue to function until another ground fault occurred on a different system conductor, in which case OCPD should function as intended.
 
Translation, if I may:

With an ungrounded system, the first unintentional ground fault would effectively make the system behave as an intentionally-grounded system, but with uncertain voltages.

Undetected, the system would likely continue to function until another ground fault occurred on a different system conductor, in which case OCPD should function as intended.
Thank you.

I intended to get back, but MDSW is higher on the list.
 
So I was wondering if you had a delta delta transformer and one of the phase hit ground how would the current return to the source to trip the ocpd since you have no neutral ??
It won't. It's like taking a battery and connecting just one terminal to ground. Nothing happens. But if the other terminal also connects to ground, THEN current flows, and a lot of it.
 
One clarification: The presence or lack of a neutral isn't the key point here. It is the presence or lack of an intentionally grounded terminal that makes the difference.

In theory you can ground _any_ terminal of a transformer to create a grounded system; with a delta secondary you can create a corner grounded system or perhaps a 'high leg' system. Similarly, if you have a wye secondary you could leave all the terminals ungrounded and have an ungrounded system.

Code has some specific requirements; if you use the neutral as a circuit conductor it _must_ be the grounded conductor. So if you have a wye secondary and you are using the neutral you can't legally install this as an ungrounded system.

-Jonathan
 
One clarification: The presence or lack of a neutral isn't the key point here. It is the presence or lack of an intentionally grounded terminal that makes the difference.

In theory you can ground _any_ terminal of a transformer to create a grounded system; with a delta secondary you can create a corner grounded system or perhaps a 'high leg' system. Similarly, if you have a wye secondary you could leave all the terminals ungrounded and have an ungrounded system.

Code has some specific requirements; if you use the neutral as a circuit conductor it _must_ be the grounded conductor. So if you have a wye secondary and you are using the neutral you can't legally install this as an ungrounded system.

-Jonathan
But a delta wye transformer would since its connected to the main service with a main bonding jumper that competes the circuit ??
 
But a delta wye transformer would since its connected to the main service with a main bonding jumper that competes the circuit ??
Only if/because there is a secondary system line, usually the neutral, that we "always" intentionally ground.

The premises EGC system is always grounded. The secondary system is usually, but not always grounded.

Tying the EGC system to the neutral assures that a line-to-ground fault behaves like a line-to-neutral fault.
 
But a delta wye transformer would since its connected to the main service with a main bonding jumper that competes the circuit ??

You can install a main bonding jumper on the delta secondary of a delta:delta transformer.

The main bonding jumper is what creates the system grounding and completes the return current path, not the presence or absence of the neutral.

-Jonathan
 