Delta Delta transformer

The electron man

Senior Member
Location
Nyc
Occupation
Electrician
So I was wondering if you had a delta delta transformer and one of the phase hit ground how would the current return to the source to trip the ocpd since you have no neutral ??
 

LarryFine

Master Electrician Electric Contractor Richmond VA
Location
Henrico County, VA
Occupation
Electrical Contractor
It waited for the second to hit it.
Translation, if I may:

With an ungrounded system, the first unintentional ground fault would effectively make the system behave as an intentionally-grounded system, but with uncertain voltages.

Undetected, the system would likely continue to function until another ground fault occurred on a different system conductor, in which case OCPD should function as intended.
 
Location
NE (9.06 miles @5.9 Degrees from Winged Horses)
Occupation
EC - retired
Translation, if I may:

With an ungrounded system, the first unintentional ground fault would effectively make the system behave as an intentionally-grounded system, but with uncertain voltages.

Undetected, the system would likely continue to function until another ground fault occurred on a different system conductor, in which case OCPD should function as intended.
Thank you.