I just want to clarify that this is very common and not prohibited. . I am not disagreeing with the other responses, just keep in mind in practice you can likely connect much more than 5% of 120v loads if they are relatively balanced across the center tap.
I just want to clarify that this is very common and not prohibited. . I am not disagreeing with the other responses, just keep in mind in practice you can likely connect much more than 5% of 120v loads if they are relatively balanced across the center tap.
Look at it this way:. Take your typical 75 kva 480 - 120/240 three phase transformer. 5% of 75kva is about 31 amps at 120. Many different situations and variables of course, but for most situations I come across, I'm not too worried about the center tap seeing more than that considering diversity and "cancelling" of neutral load from opposite phases.This is interesting.
For example: How much neutral load could you put on a 3ph 120/240v standard dry type transformer with a lighting tap?
How can you balance 120v loads across the center tap if you only have 1 wild leg and not using 2 opposing phases?
Jap>
So having 10% of a single core transformer kVA on 120V loads will have absolutely no risk of exceeding the 5% unbalance limit. Diversity may be applied to exceed that as electrofelon says, but the specific loads should be considered more carefully in this case.The 5% loading comes into play with a single core transformer which are not real common in large sizes,but are not rare in the smaller sizes like 30kVA.
The problem with exceeding the 5% limit is partly due to the issue of simply turning loads off, thereby creating an imbalance, which is fairly likely to occur when used to supply general lighting and receptacle loads.
So having 10% of a single core transformer kVA on 120V loads will have absolutely no risk of exceeding the 5% unbalance limit. Diversity may be applied to exceed that as electrofelon says, but the specific loads should be considered more carefully in this case.
In electrofelon's example, he talks about 'cancelling of neutral loads', my comment is about issues when no cancelling can possibly occur.
Sorry. I did not mean the 5% as being a relative amount of unbalance, but I can see in retrospect it might've been interpreted that way. I was referring the limit of 5% of the transformer kVA rating on loading applied to the center tap, which results from unbalanced 120V loads. But I should have stated that more explicitly and clearly.I said nothing about a 5% unbalance.
I said the 5% loading limit is due to a problem with unbalance, often caused simply by turning off loads.
In electrofelon's example, he talks about 'cancelling of neutral loads', my comment is about issues when no cancelling can possibly occur.