I need you to assist here in verifying all your 3 phase kitchen equipment, which supply power from A panel to be powered by a 120/240V delta high leg C phase electrical service. They cannot have controls powered by C phase which is the high leg and meters 240V from phase to ground.
This needs to be confirmed for any single phase or 3 phase piece of equipment powered out of the 3phase 600amp panel A with Delta High Leg on C.
How do I know if an equipment has an control wiring?
Since the equipment cut sheet calls out for a 240V/3P or 240/1P
If there is equipment under the hood and requires a shut trip breaker, should I just make the whole Panel a Shut Trip Panel instead
This needs to be confirmed for any single phase or 3 phase piece of equipment powered out of the 3phase 600amp panel A with Delta High Leg on C.
How do I know if an equipment has an control wiring?
Since the equipment cut sheet calls out for a 240V/3P or 240/1P
If there is equipment under the hood and requires a shut trip breaker, should I just make the whole Panel a Shut Trip Panel instead