Re: Delta High Leg
The March 1995 issue of EC&M magazine had a Reader's Quiz edited by a Robert J Lowrie, one of the questions of which asked this very same question.
In theory it is possible but it cannot be accomplished with standard panelboards. If you think about it you would be taking power from the high leg to the neutral of the "lighting tap" which is, with almost all certainty grounded. How would you protect it with a listed panel?
One of the respondents, J.F.F.,goes on to say " Code wise, there is no direct prohibition of such a 208v connection; but it could not be done by any "proper" connection to the panelboard of such systems."
Also, another respondent, E.D., brought up another point. You get 208v from the high leg to the lighting tap neutral. Then you have the lighting tap which also uses the neutral, 240 L-L and 120v each line to that same neutral. He points out that the NEC prohibits the mix of neutrals of different systems.