Looking at a load calculation provided by EC for a plant upgrade. The service will continue to be 4 wire, 240 three phase from a POCO closed delta overhead bank. His calculation sheet is using L1-120, L2-208 and L3-120.
On this calculation sheet the EC is using L2-208 as one leg to serve half of 240 volt single phase circuits. I have never done delta calculations this way. I do not believe this type of service was intended to be used like this. I have always served single phase from the two 120 volt legs and the only time the 208 high leg was used was when a three phase breaker was used that covered all three legs. I am not aware of a physical block that will keep him from using the 208 leg as proposed. Is there an NEC rule that would allow/not allow this? If I am sizing transformers to serve this load, his calculation method will force the EC to get it right and the POCO will have a hard time sizing transformers to serve the load correctly.
ActionDave and infinity have written in separate post that the EC proposed method is acceptable. I have never even considered his method until today and always loaded 2/3 of the single phase load on the lighter transformer.
http://forums.mikeholt.com/showthread.php?t=173696&highlight=Delta+load+calculation+using+208+High+leg+for+single+phase+240+circuits
http://forums.mikeholt.com/showthread.php?t=170172&highlight=Delta+load+calculation+using+208+High+leg+for+single+phase+240+circuits
Do I have it all wrong?
On this calculation sheet the EC is using L2-208 as one leg to serve half of 240 volt single phase circuits. I have never done delta calculations this way. I do not believe this type of service was intended to be used like this. I have always served single phase from the two 120 volt legs and the only time the 208 high leg was used was when a three phase breaker was used that covered all three legs. I am not aware of a physical block that will keep him from using the 208 leg as proposed. Is there an NEC rule that would allow/not allow this? If I am sizing transformers to serve this load, his calculation method will force the EC to get it right and the POCO will have a hard time sizing transformers to serve the load correctly.
ActionDave and infinity have written in separate post that the EC proposed method is acceptable. I have never even considered his method until today and always loaded 2/3 of the single phase load on the lighter transformer.
http://forums.mikeholt.com/showthread.php?t=173696&highlight=Delta+load+calculation+using+208+High+leg+for+single+phase+240+circuits
http://forums.mikeholt.com/showthread.php?t=170172&highlight=Delta+load+calculation+using+208+High+leg+for+single+phase+240+circuits
Do I have it all wrong?