I have a client who is requesting a transformer: 500kVA, 480V delta primary, 240V delta secondary. The transformer will be supplied from a 480/277V, 3-phase, 4 wire switchboard (neutral to ground bond in the switchboard) and will exclusively supply a DC plant with non-isolated rectifiers, 240V, 3-phase input, no 120V loads, no neutral required for the loads. The output of the DC plant is going to be 380VDC, with a high resistance midpoint ground (HRG) which will limit the line to ground voltage to 190VDC and the HRG will limit the ground fault current. The client has requested a delta to delta transformer because they do not want a neutral to ground bond and ground electrode installed on the AC side of the DC plant. Their concern is that the solidly grounded wye output would defeat the current limiting characteristics of the HRG on the DC side of the plant, causing a worker to be exposed to higher ground fault current.
My question is, whether or not we are required by the NEC to ground the delta to delta transformer as a separately derived system, or can we just rely on the equipment grounding conductors as a continuous path back to the main 480/277V, 3-phase, 4 wire switchboard?
My question is, whether or not we are required by the NEC to ground the delta to delta transformer as a separately derived system, or can we just rely on the equipment grounding conductors as a continuous path back to the main 480/277V, 3-phase, 4 wire switchboard?