I have an industrial customer who I am adding a sub-panel for. He often buys large equipment himself from a source we have used for years and I install and provide everything else.
The building has two services, one 480, one 208/120. Both are wye services. The equipment being fed is 30 KVA and rated for 200-240 volts.
We are running out of room so I am feed this panel from the 480 service through a transformer.
His supplier sent us a transformer listed for a delta primary and wye secondary. I know you can hook a wye source to the primary, but I am curious about whether I am connecting my secondary properly. Do I not have to bond from the 0(N) secondary terminal in the transformer to the grounding electrode conductor? In this case I have both a grounding conductor coming from the 480v feed, and I have solid building steel just a couple feet away.
Thanks!
The building has two services, one 480, one 208/120. Both are wye services. The equipment being fed is 30 KVA and rated for 200-240 volts.
We are running out of room so I am feed this panel from the 480 service through a transformer.
His supplier sent us a transformer listed for a delta primary and wye secondary. I know you can hook a wye source to the primary, but I am curious about whether I am connecting my secondary properly. Do I not have to bond from the 0(N) secondary terminal in the transformer to the grounding electrode conductor? In this case I have both a grounding conductor coming from the 480v feed, and I have solid building steel just a couple feet away.