Hello everyone:
is it common that the utility can distribute 240/120V, single phase (for residential loads) from Delta 3-Ph, 4-Wire transformer? I have a situation where the utility wants to provide a 240V/120V single phase service to 5-trailers each will require (150A, 240/120V, 1-ph). Since the only way to get 120/240V service is from the A-C & neutral (center tap). I have additional questions:
1. Does the main service distribution panel needs to be 240V, 3-Ph, 4-wire, and we only use the C-A phase & neutral to serve all these loads? Or the main distribution panel service needs to be single phase since it will only utilize C-A phase & neutral?
2. My understanding for the 240/120V, 3Ph, 4-W system we can't have 120V loads more than 5% of the transformer rated KVA and I'm sure this will exceed that but the utility co saying they have no concerns of that. Is this accurate statement?
Thanks in advance!
is it common that the utility can distribute 240/120V, single phase (for residential loads) from Delta 3-Ph, 4-Wire transformer? I have a situation where the utility wants to provide a 240V/120V single phase service to 5-trailers each will require (150A, 240/120V, 1-ph). Since the only way to get 120/240V service is from the A-C & neutral (center tap). I have additional questions:
1. Does the main service distribution panel needs to be 240V, 3-Ph, 4-wire, and we only use the C-A phase & neutral to serve all these loads? Or the main distribution panel service needs to be single phase since it will only utilize C-A phase & neutral?
2. My understanding for the 240/120V, 3Ph, 4-W system we can't have 120V loads more than 5% of the transformer rated KVA and I'm sure this will exceed that but the utility co saying they have no concerns of that. Is this accurate statement?
Thanks in advance!