Similar to my post on Friday, I have a question about what I think is a questionable result in an App.
Scenario is this: a 240V mid tap transformer secondary has a mix of loads on it, for simplicity sake, let's just say there are 3kVA on one of the 120V legs, and 4kVA on the other.
This is a link to an image... (sorry, seems that the new update to the forum has made it not possible to upload images??)
https://ibb.co/qnFz1R1
The transformer primary could be Delta or Wye... in both cases, the end result is that the load is carried over to the associated line, such that
Line A reports that it has 3kVA
Line B reports that it has 4kVA
And, in both cases, it is computing the current by dividing by 277, resulting in
10.83A on A
14.44A on B
For the Wye case, this seems correct.. is it?
For the Delta case, there is one circuit, wouldn't both conductors have the same current? (7000VA/480V = 14.58A)?
(I think the answer to this is yes... same case as https://forums.mikeholt.com/forum/a...ent-on-primary-side-of-center-tap-transformer - the transformer doesn't care if it is a single transformer, or one of three transformers in a 3-phase transformer... correct?)
Scenario is this: a 240V mid tap transformer secondary has a mix of loads on it, for simplicity sake, let's just say there are 3kVA on one of the 120V legs, and 4kVA on the other.
This is a link to an image... (sorry, seems that the new update to the forum has made it not possible to upload images??)
https://ibb.co/qnFz1R1
The transformer primary could be Delta or Wye... in both cases, the end result is that the load is carried over to the associated line, such that
Line A reports that it has 3kVA
Line B reports that it has 4kVA
And, in both cases, it is computing the current by dividing by 277, resulting in
10.83A on A
14.44A on B
For the Wye case, this seems correct.. is it?
For the Delta case, there is one circuit, wouldn't both conductors have the same current? (7000VA/480V = 14.58A)?
(I think the answer to this is yes... same case as https://forums.mikeholt.com/forum/a...ent-on-primary-side-of-center-tap-transformer - the transformer doesn't care if it is a single transformer, or one of three transformers in a 3-phase transformer... correct?)