I am hooking up a 208v delta to 480 wye transformer for 480v x-ray equipment. My question is; do I need to bond the H0 and just leave it unused?:?
I am hooking up a 208v delta to 480 wye transformer for 480v x-ray equipment. My question is; do I need to bond the H0 and just leave it unused?:?
Well, I took the OP at his word that he has a 208 delta primary X 480/277Y secondary. That would mean to me that he means the H0 termininal is on the 480Y side. I would be willing to bet that the specs for the xray machine call for a connection to a solidly grounded 480/277Y system.
X-ray equipment does not require a neutral it is strictly 480v, I suspect the delta wye transformer was ordered because of cost considerations but I don't really know. Service to building is 208/120 3 phase, transformer is fed strictly 208v on X1, X2, and X3 and has H1, H0, H2, H3 outputs.
Sounds like you have the right type of transformer. By the way, this would likely be a little more expensive transformer than a more common 480 delta X 208/120Y transformer due to volume of sales. The point I was trying to make about the neutral is that the machine likely needs to be fed by a 480 solidly grounded Y system even if it does not need a neutral. Many things are like this, such as some VFD's. Ungrounded and corner grounded 480 delta systems are getting even more rare.