I'm going to go out on a limb and say I disagree with charlie b. I believe he is confusing the issue with an open delta arrangement. The arrangement you are inquiring about is loading 2 of 3 wye Lines. IMO you will have full usage of 67% for Line to Neutral loads, 33% for Line to Line loads, and somewhere in between for a combination of such loads.brentp said:My original post had alot to be desired information wise. What I really am asking for help with is the formula/calculation showing why the transformer can only be loaded to 57% as Charlie B stated. My electrical theory needs some work.
After considering this further, I have a question: Isn't Line to Line current and voltage 30? out of phase with the winding voltage? As such, I don't see how the full 312A is available for Line-to-Line loads.jim dungar said:Because each winding in a wye connected transformer is fully rated you can get 112.5kVA/(208V*1.73) = 312A from each secondary line.
Time for fun with numbers:
If you have (2) 120V loads connected line to neutral you will be using 624A out of the possible full load 936A which agrees with the 67% mentioned by Smart $.
But, if your load is (1) 208V load, you will be using 208*312 = 65kVA out of the possible 112.5kVA available which is the 57.7% mentioned by Charlie B.