We are beginning work for a new client - fitness centers - and we are wondering if anyone is familiar with any NEC code language that would allow us to take a reduced demand or diversity load on large groups of electrically-powered same-type fitness equipment (similar to the demand factors for commercial kitchen equipment when there are 6 or more pieces of cooking equipment). We have not seen anything in the code.
The specific question is this - the fitness center has as many as 20 to 30 treadmills, each requiring a dedicated 20 amp circuit (equipment nameplate says FLA = 16 at 120 V). From experience, we have rarely (or never) seen all of the treadmills operating at one time, and anticipate that even if every one were operating, they would likely not all be operating at maximum speed. That being the case, we are wondering if we are permitted to take a reduced load for the combined equipment at the feeder or service level, while still providing individual 20 amp circuits to each piece of equipment.
Any help or thoughts would be very much appreciated.
The specific question is this - the fitness center has as many as 20 to 30 treadmills, each requiring a dedicated 20 amp circuit (equipment nameplate says FLA = 16 at 120 V). From experience, we have rarely (or never) seen all of the treadmills operating at one time, and anticipate that even if every one were operating, they would likely not all be operating at maximum speed. That being the case, we are wondering if we are permitted to take a reduced load for the combined equipment at the feeder or service level, while still providing individual 20 amp circuits to each piece of equipment.
Any help or thoughts would be very much appreciated.