SmithBuilt
- Foothills of NC
An existing school building, has 6 gas/AC RTU's. The hvac contractor wants to install 20 VAV boxes total kw 122. The total AC load is 91kw.
During the winter the A/C compressors will not be running. The gas furnace would still be used. The VAV boxes would only come on if 1 or 2 rooms needed heat, if most of the rooms needed heat the gas furnace would meet the needs and not the VAV's. It is possible all the VAV's could run at once, but the AC compressors would not be running just the blowers.
Knowing the compressors would not be running in the winter is it permissible to use that available wattage for the VAV boxes?
Any suggestions on how to calculate per NEC? I would say additional load but its not really.