Jennifer K.
Member
- Location
- Chicago, IL, USA
Hello - I am curious to see if anyone here has used NEC 430.26 to apply demand factor(s) to motors such as those that may be used in a process/manufacturing type facility? The code indicates "Where reduced heating of the conductors results from motors operating on duty-cycle, intermittently, or from all motors not operating at one time, the authority having jurisdiction may grant permission for feeder conductors to have an ampacity less than specified in 430.24...." In the handbook version there is a highlighted informational text box below this section that further indicates that AHJ may grant permission to allow a demand factor of less than 100%. Motors not running at the same time is completely clear to me - then the non-coincidental load section would apply and the smaller load could be dropped when sizing the feed however I am trying to figure out if anyone utilizes this section to apply other factors (for example 75%, 80%, etc.) to a motor load? It seems as though one would need detailed knowledge of the motor(s) in consideration to apply these demand factors and even in that case it would still be a complete estimation by the engineer (a cut sheet for the motor likely would not have a demand factor on it). Thanks in advance for any responses!