Demand factor for the load of fire/life safety systems

TMMB

Senior Member
Location
EGYPT
Occupation
Electrical Manager
Is there in NFPA any article talking about demand factor for the electrical loads of the Fire/life systems
is demand factor can be applied on the loads of fire/life safety system
 
Is there in NFPA any article talking about demand factor for the electrical loads of the Fire/life systems
is demand factor can be applied on the loads of fire/life safety system
700.4(A)
Demand factor=1
 
Thx for your reply but i checked the article but unfortunately i didn't find the same content
700.4 Capacity and Rating.
(A) Capacity. An emergency system shall have adequate
capacity in accordance with Part' I through IV of Article 220 or
by another approved method. The system capacity shall be
sufficient for the rapid load changes and transient power and

energy requirement" asociociatcd "id1 any expected loads
 
Thx for your reply but i checked the article but unfortunately i didn't find the same content
700.4 Capacity and Rating.
(A) Capacity. An emergency system shall have adequate
capacity in accordance with Part' I through IV of Article 220 or
by another approved method. The system capacity shall be
sufficient for the rapid load changes and transient power and

energy requirement" asociociatcd "id1 any expected loads
This one help?:
Nec 2017 section 700.4 | Information by Electrical Professionals for Electrical Professionals https://forums.mikeholt.com/threads...n,for all loads to be operated simultaneously.
 