A Adnan Hasan Member Location baghdad, Iraq Apr 25, 2013 #1 Dears.. what's the demand factor of lighting for hospital? is table 220.42 applicable? thank you
C CONDUIT Senior Member Apr 25, 2013 #2 Yes! You can use the demand factors in table 220.42. Just make sure that you look at the note below the table.