What is the demand factor when sizing panel feeder for rectifier used in telecommunication tower per nec 2014?
What is the demand factor when sizing panel demand load calculation for rectifier used in telecommunication tower per nec 2014?
How do you determine if ac panel is not overloaded then? Are you saying demand factor for AC feeding ac part of rectifiers is 0? Please helpThere is no demand factor or diversity factor for cell tower rectifiers.
Nearly every cell tower I have worked on has come with a pre wired shelter and a 200A panel. We run a 200A service to most of them because that's what's speced.
There is no demand factor or diversity factor for cell tower rectifiers.
Nearly every cell tower I have worked on has come with a pre wired shelter and a 200A panel. We run a 200A service to most of them because that's what's speced.
How do you determine if ac panel is not overloaded then? Are you saying demand factor for AC feeding ac part of rectifiers is 0? Please help
Sent from my SM-G935U using Tapatalk
Qcroanke (one of our members) builds, installs , and maintains those type of shelters/buildings IIRC.
I believe they are telling you that the loads will not be on at the same time. Either/Or, not both.I have the following panel schedule and when it says total noncoincidental load adjusted service load 0 watts is that correct or should it be more then 0 watts? Also entire panel sechdule total adjusted load is it correct, it does not take into consideration noncoincidental load?
Yea I understand that but loads that are on are not taken into consideration. See at bottom total load is 41.45kw but when you add 6.2kw + 35.25kw + 17.6kw = 59.05 kw not 41.45kw. Should total adjusted load not be 59.05kw?I believe they are telling you that the loads will not be on at the same time. Either/Or, not both.
Why are you adding 17.6 kw when it will not be on when the larger loads are?Yea I understand that but loads that are on are not taken into consideration. See at bottom total load is 41.45kw but when you add 6.2kw + 35.25kw + 17.6kw = 59.05 kw not 41.45kw. Should total adjusted load not be 59.05kw?
I have attached zoom image of load:
What the note says 4x4400 = 17600 watts are noncoincidental or not on but 5x4400 = 22000 watts are on. So total adjusted load be 22000 + 6200+ 35250 = 63450 watts?Why are you adding 17.6 kw when it will not be on when the larger loads are?