There is no demand factor or diversity factor for cell tower rectifiers.

Nearly every cell tower I have worked on has come with a pre wired shelter and a 200A panel. We run a 200A service to most of them because that's what's speced.
How do you determine if ac panel is not overloaded then? Are you saying demand factor for AC feeding ac part of rectifiers is 0? Please help

Sent from my SM-G935U using Tapatalk
 
There is no demand factor or diversity factor for cell tower rectifiers.

Nearly every cell tower I have worked on has come with a pre wired shelter and a 200A panel. We run a 200A service to most of them because that's what's speced.

Qcroanke (one of our members) builds, installs , and maintains those type of shelters/buildings IIRC.
 
When the batteries go into a deep discharge due to a power outage (if there is a standby gen, it may not start for some reason), the rectifiers, including any redundant ones, go into full recharge of the batteries and carrying the telephone technology load. Unless there is a current limit setup special on that system, there is no demand factor.

One of the cellphone companies I work with call it a dark office load (DOL) condition and often is 2 x the normal load because they also consider redundant HVAC coming on to cool the environment that would have been overheating during that time.
 
How do you determine if ac panel is not overloaded then? Are you saying demand factor for AC feeding ac part of rectifiers is 0? Please help

Sent from my SM-G935U using Tapatalk

I'm saying that the shelter is set up and wired to handle the connected load the same as any building.

Diversity factors are a special area of the code for multi family dwellings and appliances mostly.
 
Qcroanke (one of our members) builds, installs , and maintains those type of shelters/buildings IIRC.

Yep. We've chatted about them on occasion.

200A service with about 60A of total load and that includes the air conditioners. The only 120V loads are the lights and some convenience receptacles that only get used when someone is there so it's a good thing they make us pull full sized neutrals.
 
I have the following panel schedule and when it says total noncoincidental load adjusted service load 0 watts is that correct or should it be more then 0 watts? Also entire panel sechdule total adjusted load is it correct, it does not take into consideration noncoincidental load?
 

Attachments

  • Panel sechdule.jpg
    Panel sechdule.jpg
    127 KB · Views: 3
I have the following panel schedule and when it says total noncoincidental load adjusted service load 0 watts is that correct or should it be more then 0 watts? Also entire panel sechdule total adjusted load is it correct, it does not take into consideration noncoincidental load?
I believe they are telling you that the loads will not be on at the same time. Either/Or, not both.
 
I believe they are telling you that the loads will not be on at the same time. Either/Or, not both.
Yea I understand that but loads that are on are not taken into consideration. See at bottom total load is 41.45kw but when you add 6.2kw + 35.25kw + 17.6kw = 59.05 kw not 41.45kw. Should total adjusted load not be 59.05kw?

I have attached zoom image of load:
 