I'm doing a service load calc for a shower house and was looking at the code book but couldn't find any demand factors for any of the equipment. This type of structure doesn't fall under anything listed in the code book in Article 220 so I guess I just use the data for all the individual equipment and add it up with no demand factors? Here's my list of equipment:
120/208V 3ph.
2 each Water Htr @ 54kw, 3ph, 208V
4 each Hand Dryer @ 20a, 1ph, 120V
2 each unit heaters @ 3kw, 1ph, 208V
4 each unit heaters @ 1.5kw, 1ph, 120V
1 exhaust fan @ 4.8a, 1ph, 120V
2 parking lot lights @ 180VA 1ph, 208V
3 exterior lights @ 180VA 1ph, 120V
21 fluorescent lts. @ 180VA, 1ph, 120V
5 receptacles @ 180VA, 1ph, 120V
My calcs say I need a 600a service but there's another shower facility on the same grounds that has a load nearly the same as this one but is fed by a 400a service. That's why I was wondering if I'm missing someting or if they just undersized the service at the other facility.