This is going to be a decently sized question for my post here so lets see if I can get it and it make sense when I am done.
(refering to commercial applications)
We are looking at sizing feeders and trying to decide what load to use to size the feeders. I have read the rule in the NEC that says that the load is 100% of non-continuous load and 125% of continuous load. Does the non-continuous load in that statement allow me to size the wire for only the 65% of kitchen equipment load or do I have to use the full 100% of all the kitchen load on my feeder sizing. The same would be asked to the discounts given for receptacles. If the answer is is 100% of non-continuous and 125% of continuous no matter what then do my main breakers need to be sized that way to, and what is the point of the discounts when all is said and done, can I not just size the wire for the overcurrent protection protecting that wire?
(refering to commercial applications)
We are looking at sizing feeders and trying to decide what load to use to size the feeders. I have read the rule in the NEC that says that the load is 100% of non-continuous load and 125% of continuous load. Does the non-continuous load in that statement allow me to size the wire for only the 65% of kitchen equipment load or do I have to use the full 100% of all the kitchen load on my feeder sizing. The same would be asked to the discounts given for receptacles. If the answer is is 100% of non-continuous and 125% of continuous no matter what then do my main breakers need to be sized that way to, and what is the point of the discounts when all is said and done, can I not just size the wire for the overcurrent protection protecting that wire?