Hi Everyone,
I'm an architect / builder working on a new spec house prototype and I was hoping to get some guidance on how to determine the overall demand load for the electrical panel. I'm pretty well versed in FBC and navigating code in general, but I'm new to electrical design and NFPA 70A has been a bit challenging.
I've put together my panel schedule and figured out all of my connected loads , but I cant seem to figure out which demand factors to apply to which connected loads in order to determine the total demand load for the panel. I've linked a working copy of the plans and schedules. Any insight would be appreciated.
Linked Plan & Schedules - Please disregarding circuit callouts on plans. That was a first pass and has not been updated to match the linked panel schedule
Connected Loads
I'm an architect / builder working on a new spec house prototype and I was hoping to get some guidance on how to determine the overall demand load for the electrical panel. I'm pretty well versed in FBC and navigating code in general, but I'm new to electrical design and NFPA 70A has been a bit challenging.
I've put together my panel schedule and figured out all of my connected loads , but I cant seem to figure out which demand factors to apply to which connected loads in order to determine the total demand load for the panel. I've linked a working copy of the plans and schedules. Any insight would be appreciated.
Linked Plan & Schedules - Please disregarding circuit callouts on plans. That was a first pass and has not been updated to match the linked panel schedule
Connected Loads
- Lighting: 1.25 KVA
- Receptacles: 9.42 KVA
- Only includes 110V receptacles
- Motors: 0.90 KVA
- (2) 50W exhaust fans (Not sure if this is miscategorized. I've sometimes seen it listed under lighting)
- (1) 800W Garage Door Opener.
- AC: 1.3 KVA
- AHU only
- Heating: 5.0 KVA
- Supplemental heat kit only. Condensing unit omitted as non-coincidental.
- Kitchen: 16.05 KVA
- Includes small appliance circuits plus all kitchen appliances.
- Should kitchen appliances be included here or should they be included under receptacles?
- Includes small appliance circuits plus all kitchen appliances.
- Other: 12.25 KVA
- Includes water heater, dryer, washer, and smoke detectors
- Total Connected Load = 46,170 VA / 240V = 192.38 A
- This is where I'm stuck. I've been reviewing NFPA 70A for the last two days but don't understand how to get from the total connected load to the demand load.