Just did a quick search in NFPA Link and found some references to dental offices.
Dental office is a new definition in NEC 517.2. There is also a definition for Anesthetizing Location, if that applies.
517.10 Applicability - is up to the AHJ's discretion. Areas not covered are business offices , corridors and waiting rooms in dental offices.
Falls under Basic Care - Category 3 type space.
Requires taper resistant receptacles where children might be present?
406.12 Tamper-Resistant Receptacles.
All 15- and 20-ampere, 125- and 250-volt nonlocking-type receptacles in the areas specified in
406.12(1) through (8) shall be listed tamper-resistant receptacles.
(1)Dwelling units, including attached and detached garages and accessory buildings to dwelling units, and common areas of multifamily dwellings specified in
210.52 and
550.13
(2)Guest rooms and guest suites of hotels, motels, and their common areas
(3)Child care facilities
(4)Preschools and education facilities
(5)Business offices, corridors, waiting rooms and the like in clinics, medical and
dental offices, and outpatient facilities
517.45 Essential Electrical Systems for Other Health Care Facilities.
(A) Essential Electrical Distribution.
If required by the governing body, the essential electrical distribution system for
Category 3 (basic care) patient care spaces shall be comprised of an alternate power system capable of supplying a limited amount of lighting and power service for the orderly cessation of procedures during a time normal electrical service is interrupted.
Informational Note:
See NFPA 99-2018,
Health Care Facilities
From personal experience, they have all seemed exactly like a normal business office.