Depth of Cover

hyattjay

Member
Location
CO.
Occupation
Engineer
Is there a hard and fast maximum depth of cover for direct burial feeders (transformer to distribution panel)? Our team is looking at the options including OH and UG, with and without conduit/raceway.
 

ron

Senior Member
I think Larry mean 300.5 for the minimum cover requirements for <1000V.

Maximum depth is not established, except if the feeder is critical, I would suggest doing Neher McGrath calculations, as the deeper you get, the more of a derate on the conductor ampacity gets, due to difficulty in emitting heat to the environment.
 

hyattjay

Member
Location
CO.
Occupation
Engineer
Correct, the Depth of Cover will be 36" from top of the cable to top of finished grade. Cable will be on 3" of fine sands, covered by 6" of fine sands, then back filled to top of finished grade, a red warning tape is installed 12" above the cable (If I recall the detail from the contractor correctly).
 

infinity

Moderator
Staff member
Location
New Jersey
Occupation
Journeyman Electrician
Correct, the Depth of Cover will be 36" from top of the cable to top of finished grade. Cable will be on 3" of fine sands, covered by 6" of fine sands, then back filled to top of finished grade, a red warning tape is installed 12" above the cable (If I recall the detail from the contractor correctly).

I don't think that you can do better than that for direct burial. :)
 