You are mixing systems. NFPA 780 is for lightning protection and it’s a structural ground. If you read the rest of the Code it should also be separate from the power system. NEC is system grounding and part of the power system. It has only incidental lightning protection and primarily is intended to absorb indirect effects such as a lightning strike to the incoming service wiring.
In addition in most jurisdictions NFPA 70 is legally required. NFPA 780 is an engineering standard.
As far as the engineering of the system ground rings are a ridiculous waste of money. The only advantage is that it makes it easy for the dirt diggers and the steel monkeys to understand without screwing it up. The effectiveness of a system is a combination of factors but the deity is linear with conductance while the diameter produces diminishing returns. Multiple electrodes also produce diminishing returns. Effectively a ring is just a super shallow very large diameter ground rod. A single 10 foot deep ground rod will typically produce the same resistance as the hundreds of feet of buried wire used in most rings. The only purported (and questionable) value is that since it is usually a short distance from every building column the surge impedance of the jumper is low. But this is more than made up for by the higher impedance of the grounding electrode
So in short unless you have a ufer ground condition (bad soil) just sink two rods and call it a day. Tie your J bolts into the rebar. Ignore inspections that only look for ground straps outside the structure. A slab is much more ground rod than you can possibly ask for. Mines are required to measure every ground every year. I’ve done thousands of tests. You quickly get to know what good grounding is that way.