Depth of pull box

Status
Not open for further replies.

bwyllie

Senior Member
Location
MA
What determines the depth of a pull box? Section 314.28 states the (2) min dimensions for the sides of the box based on the number and size of conduits entering the box, but where does the code refer to the depth of the box?
 
As infinity said but assuming if it is a straight or angle pull.

It also depends where the conduits enter. Take a look at 314.28(A)(2) exception 312.6(A).
 