namesfuzzy53

New member
I am getting conflicting stories from the electrical inspector and electrician on underground wiring from the house to spa. Electrician installed line appx 8-10"
in ground. Inspector says must me 19-20". Electrician says no, not if I am laying 4" concrete slab over the area, which I am. Inspector says not okay and electrician wants more money to come out and put it down deeper.

What does the national code say?: I'm getting tired of the run around
 

roger

Moderator
Staff member
Location
Fl
Occupation
Retired Electrician
Click Here and navigate your way to 300.5 and 680.10 between to two tables you should be able to find what applies to this installation.