Hello,
Here is a post talking about depth of Pull Box caluclation. Great graphic posted but the discussion was about a "Removable Cover".
The NEC makes a distinction between Removable cover and Hinged cover elsewhere.
How does this effect pullbox depth calculations for pull boxes that have a hinged cover and not removable (I suppose for both conductors leaving opposite wall and those not leaving opposite wall)?
Here is a post talking about depth of Pull Box caluclation. Great graphic posted but the discussion was about a "Removable Cover".
Pullbox Sizing
I have an installation where (3) 4" EMT conduits will be entering a pullbox from the bottom, and exiting out the back (at the top) Assuming that I'm correct that since the conductors don't exit directly across from each other, the calculation would be (6x4")+4"+4" = 32" so a 32" x 32" box. My...
forums.mikeholt.com
The NEC makes a distinction between Removable cover and Hinged cover elsewhere.
How does this effect pullbox depth calculations for pull boxes that have a hinged cover and not removable (I suppose for both conductors leaving opposite wall and those not leaving opposite wall)?