I would run at least 3/4" PVC if I was going to put 12/2 UF in it.I am putting a 120v service to my shed. using UF wire in 1/2pvc what is the min. depth I should go?
I will ask why you want to run UF in PVC, if you are running PVC I would suggest using single conductors type THWN in the PVC.Column 4 Residential Branch Circuits Rated 120 Volts or Less with GFCI Protection and Maximum Overcurrent Protection of 20 Amperes
You should take a look at the top row "All locations not specified below" and column 4.Originally posted by shockare:
Should read
"18" deep if WITH GFCI protection on the circuit."
The 12" depth rule is for locations that will have a concrete cover from 2 to 4 inches of concrete
Good idea, not an NEC requirement.A red electrical caution tape must also be install in the trench prior to the final cover
Yes very true, but a 120 volt branch circuit is not service conductors, so it does not apply to this installation, still a good idea though.Originally posted by shockare:
Iwire take a look at 305 (1) 3
Service Conductors, Underground service conductors that are not encased in concrete and that are buried 450 mm (18")or more below grade shall have their location identified by a warning ribbon that is placed in the trench at least 300mm
(12") above the underground installation
Can you explain why you think column 4 does not apply to the circuit we are taking about?Column 4 is residential branch ckts 120v or less With gfi protection.
Golf4life is Not going under a building, nor driveway,road. He is useing the pvc pipe as a sleeve so then column 3 must apply
I would think this is a 20 amp circuit as he wants to put it in 1/2" PVC.I am putting a 120v service to my shed. using UF wire in 1/2pvc what is the min. depth i should go?
Bob12" Deep if you follow the rules of column 4 of Table 300.5