I'm looking in article 220 for service calculations and I see that in a dwelling unit A/C's are supposed to be sized at 100%. I'm currently working on a commercial building that has decided to put in (4) 5 Ton split units. The A/C condenser will be fed from downstairs. The heater coil and air handler will of course be up in the attic. I'm trying to figure out my total KVA for the floor so I can size my feeder and cannot find anything for derating units for commercial use. Also, Art. 440 doesn't reference any derating or at least that I'm noticing.
This is what all the units will be. I'm also a little confused (which is easily done) about the Min Circ. Ampacity and Max OCPD. Shouldn't they be listed by from 208/240V? Things just really don't seem kosher from what I'm looking at. I called the A/C guy today and he said that he needed (2) 60A breakers for the air handler..... I'm pretty sure he was wrong lol.
The Air Handler model # is WH1T6021STANJA
This is what all the units will be. I'm also a little confused (which is easily done) about the Min Circ. Ampacity and Max OCPD. Shouldn't they be listed by from 208/240V? Things just really don't seem kosher from what I'm looking at. I called the A/C guy today and he said that he needed (2) 60A breakers for the air handler..... I'm pretty sure he was wrong lol.
The Air Handler model # is WH1T6021STANJA
Heater Model # | Heater kW (208/240V) (480V) | PH/HZ | No. Elements kW Per | Type Supply Circuit Single Circuit Multiple | Circuit Amps. | Motor Ampacity | Minimum Circuit Ampacity | Maximum Circuit Protector |
RXBH-1724A15J | 10.8/14.4 | 1/60 | 3 - 4.8 | SINGLE | 51.9/60 | 4.1 | 70/81 | 70/90 |
RXBH-1724A15J | 3.6/4.8 | 1/60 | 1 - 4.8 | MULTIPLE CKT 1 | 17.3/20 | 4.1 | 27/31 | 30/35 |
RXBH-1724A15J | 7.2/9.6 | 1/60 | 2 - 4.8 | MULTIPLE CKT 2 | 34.6/40 | 0 | 44/50 | 45/50 |