Designer101
Senior Member
- Location
- California
- Occupation
- Solar and ESS Designer
I have encountered a situation, where we have to do feeder tap into the existing sub panel 225A, and its connected to split phase 400A rated main panel onto one of 200A main disconnect. the existing feeder wires are rated 2/0 ONLY, But the temperature where PV is installed is usually high and we have to used derate factor of at least 0.87.
. my question is how are under ground feeder wires derating calcs done? is it separate for the wiring calcs thats are done on ambient temperature? Or the calcs is done similar.
example 200 A of Service wires ( ambient temperature is usually 100 degrees F ON MOST OF SUMMER)
THWN-2
(3)Awg #3/0
ampacity 225*0.87=195.75A, i used 0.91 instead of 0.87 and choose 204.75A as final derate ampacity, to argue 3/0 is sufficient.
but the existing feeder wires have only 2/0 pre wired .
I am not sure how the 2/0 wire was used as feeder between sub panel and main panel? and the inspector was okay with that. Or I m missing some major information here, I am not an electrical engineer by profession my back ground is from mechanical.
thank you
. my question is how are under ground feeder wires derating calcs done? is it separate for the wiring calcs thats are done on ambient temperature? Or the calcs is done similar.
example 200 A of Service wires ( ambient temperature is usually 100 degrees F ON MOST OF SUMMER)
THWN-2
(3)Awg #3/0
ampacity 225*0.87=195.75A, i used 0.91 instead of 0.87 and choose 204.75A as final derate ampacity, to argue 3/0 is sufficient.
but the existing feeder wires have only 2/0 pre wired .
I am not sure how the 2/0 wire was used as feeder between sub panel and main panel? and the inspector was okay with that. Or I m missing some major information here, I am not an electrical engineer by profession my back ground is from mechanical.
thank you