I have read previous posts and want to post this question for a specific scenario. Meter main outside, #2 alum ser comes in the house and through an outside wall 25', then pops out to the panel. That 25' will be encased in foam insulation. So 338.10(B)(4) brings that cable down to 75 amps on the 60 degree table in T310.15(B)(16). Is that correct?
The second scenario is similar, same cable goes up the wall 8' and into floor joists for 40' or so to panel. Previous posts seem to indicate this is also at 60 degrees and no exception (10' 10%) applies. Also correct?
Solution: if the above are correct would ser with XHHW-2 (if they make it) solve the violation? Thanks in advance for any replies.