Re: derate
Article 310 Conductors for General Wiring
Table 310.15(B)(2)(a) provides adjustment factors based on the number of current carrying conductors with reference to tables 310.16 through 310.19 .
In other words, you start with table 310.15(B)(2)(a) and find the adjustment factor you need to apply. Then you go to tables 310.16 through 310.19 (which ever applies) and find the conductor size you'll need after applying the adjustment factor.
In your case there are 12 current carrying conductors. Table 310.15(B)(2)(a) says the adjustment factor you need to apply is 50% for 10 to 20 current carrying conductors.
Your conductors will be in a raceway. Go to Table 310.16.
You need 20 amps at 50% ampacity. 10 AWG is 40 amps in the 90? C. column. 50% of that is 20 amps.
In your example you are correct. 6 twenty amp circuits in one conduit will require at least 10 AWG conductors.