I have a solar question as it relates to the NEC. We typically run ETAP with specified loading to determine the steady-state temperature of the DC conductors in order ensure it does not exceed insulation temperature limits (90°C). There is also an option in the program that determines the maximum ampacity of the DC cables before exceeding temperature limits. My question is: does this simulated max. ampacity value need be protected by the next higher standard OCPD rating?
For example, circuits are sized to be 400 kcmil Aluminum, protected with a 300A fuse. There are a bunch of direct-buried circuits in the same trench with poor soil conditions. The program results in an ampacity of 230A. This is technically not protected by the 300A fuse. Do I need to mess with the sizes/arrangement until the ampacity is greater than 250A? Meanwhile, the steady-state temp. at specified normal-loading values hit a maximum of 80°C.
I think it is a little different with PV DC circuits as well because the OCPD is mainly protecting the cable from backfeed parallel contribution in the event of a short-circuit. It is highly unlikely a short circuit will result in a value less than 250A. I guess my initial thought is NO, this ampacity value need not be protected by the fuse. Parallel contributions are always at least double the normal loading on that circuit. A short-circuit would be a quick event, and the transient temperature response will be very slow in comparison to the fuse tripping time.
Open to all thoughts, thanks!
For example, circuits are sized to be 400 kcmil Aluminum, protected with a 300A fuse. There are a bunch of direct-buried circuits in the same trench with poor soil conditions. The program results in an ampacity of 230A. This is technically not protected by the 300A fuse. Do I need to mess with the sizes/arrangement until the ampacity is greater than 250A? Meanwhile, the steady-state temp. at specified normal-loading values hit a maximum of 80°C.
I think it is a little different with PV DC circuits as well because the OCPD is mainly protecting the cable from backfeed parallel contribution in the event of a short-circuit. It is highly unlikely a short circuit will result in a value less than 250A. I guess my initial thought is NO, this ampacity value need not be protected by the fuse. Parallel contributions are always at least double the normal loading on that circuit. A short-circuit would be a quick event, and the transient temperature response will be very slow in comparison to the fuse tripping time.
Open to all thoughts, thanks!