dbailey0521
Member
- Location
- Crystal River, FL, USA
I just got turned down for derating the neutral conductor on a single phase commercial service. It is a 400 amp with two 200 amp disconnects. One is just for the AC units. The other is for the main panel. The load calc has the main panel at 135 amps and the neutral at 70 amps, but he wants a full size neutral. 220.61 "A" states the neutral must carry the maximum unbalanced load. 220.61 "B" (2) states in excess of 200 amps can be derated. When did they change this? If you follow the examples in the back of the book, they are still reducing the neutral. Can anyone give me the correct code reference?