sparkymarjon
Member
A debate came up so I thought I would bring it here, If you have, let's say 6- 2wire s.p. circuits in a conduit do you count the nuetrals for derating purposes. I feel because you have multiple different circuits in the same conduit, yes. However others feel that since they are all 2 wire circuits and the nuetral is carrying back the balance load of the hot leg,they cancel each other out and have no effect on the other conductors. I feel since there are amps in both nuetral and hot leg, there will be a heating effect when mixed with other conductors, which is why you need to count nuetrals for derating.. how do you feel