Plano12345
- United States
I'm having a discussion with an engineer. It's as follows:
We have wires for 10 current carrying conductors for 5 circuits in a 2" conduit and a bare for grounding
The size of all the wires are #8 copper.
The breaker sizes are the following: 4 at 20 amps and 1 at 30 amps. The current using the 30 amp breaker is 19 amps.
At 75 C for XHHW, you have 50 amps available for the current. Since there are 10 CCC, you really have 25 amps from derating.
My opinion is one set of wires needs to increase in size to completely cover the 30 amp breaker, so we'd make the wires for the 30 amp breaker #6. He is telling me the conductors are ok in that at 25 amps, we cover the necessary current in the design and would cover the breaker in the sense that 25 x 1.25 is greater than 30.
I always saw this as the derating current you create must cover the breaker completely.
I went to the NEC 2011 and couldn't find anything specific to what he is saying. Am I simply being too conservative? I'd rather be safe but it'd be nice to know if you confirm my colleague is 100% correct.
Thanks!
Thanks!