Hello All,
Long time user of the forum, but first time posting.
Question:
In a single 3/4" conduit of 4 current-carrying conductors rated at 90 degrees, do we need to derate using the 60 degree column of Table 310.15(B)(16) if the terminations are assumed to be rated for 60 degrees? We believe we are allowed to use the 90 degree column per the first paragraph of NEC 110.14(C).
Background:
Currently, we have a design where we have a total of four duplex NEMA 5-20R receptacles in a space with two receptacles on one circuit and the other two receptacles on another circuit. We show one 3/4" GRC conduit connecting all receptacles and one homerun to the panelboard. Each receptacle is wired with 2#12 wire and a #12 ground (90 degree rated). Each circuit is protected by a 1P20A circuit breaker. In essence, the 3/4"C homerun to the panel contains 4 current-carrying conductors.
Since there are 4 current-carrying conductors, the code requires us to derate the conductors [Table 310.15(B)(3)(a)]. Here is where the disconnect happens between us and the reviewer. In our interpretation of the code, we are allowed to derate from the 90 degree column of Table 310.15(B)(16) since our conductors are rated for 90 degrees. The reviewer is stating that since we are dealing with loads less than 100A, we need derate from the 60 degree column per NEC 110.14(A)(1). Our stance is that per the first paragraph in NEC 110.14(A) which states that the "Conductors with temperature ratings higher than specified for terminations shall be permitted to be used for ampacity adjustment, correction, or both." we can use the 90 degree column to derate in lieu of the 60 degree column. We believe we are also still in compliance with NEC 110.14(C)(1) since #12 wire is still good for a 60 degree termination since #12 at 60 degrees is rated for 20A. The lower of the two values should be used.
We are being asked to either homerun each circuit or upsize the wire to #10AWG. We don't believe this is necessary, but wanted to get your thoughts.
Thank you for the help!
Long time user of the forum, but first time posting.
Question:
In a single 3/4" conduit of 4 current-carrying conductors rated at 90 degrees, do we need to derate using the 60 degree column of Table 310.15(B)(16) if the terminations are assumed to be rated for 60 degrees? We believe we are allowed to use the 90 degree column per the first paragraph of NEC 110.14(C).
Background:
Currently, we have a design where we have a total of four duplex NEMA 5-20R receptacles in a space with two receptacles on one circuit and the other two receptacles on another circuit. We show one 3/4" GRC conduit connecting all receptacles and one homerun to the panelboard. Each receptacle is wired with 2#12 wire and a #12 ground (90 degree rated). Each circuit is protected by a 1P20A circuit breaker. In essence, the 3/4"C homerun to the panel contains 4 current-carrying conductors.
Since there are 4 current-carrying conductors, the code requires us to derate the conductors [Table 310.15(B)(3)(a)]. Here is where the disconnect happens between us and the reviewer. In our interpretation of the code, we are allowed to derate from the 90 degree column of Table 310.15(B)(16) since our conductors are rated for 90 degrees. The reviewer is stating that since we are dealing with loads less than 100A, we need derate from the 60 degree column per NEC 110.14(A)(1). Our stance is that per the first paragraph in NEC 110.14(A) which states that the "Conductors with temperature ratings higher than specified for terminations shall be permitted to be used for ampacity adjustment, correction, or both." we can use the 90 degree column to derate in lieu of the 60 degree column. We believe we are also still in compliance with NEC 110.14(C)(1) since #12 wire is still good for a 60 degree termination since #12 at 60 degrees is rated for 20A. The lower of the two values should be used.
We are being asked to either homerun each circuit or upsize the wire to #10AWG. We don't believe this is necessary, but wanted to get your thoughts.
Thank you for the help!