Re: derating and the 90* colm
dereckbc et al,
You can eliminate a lot of going back and forth and guessing if you divide the correction factors into the required ampacity, instead of arbitrarilly picking a conductor from the table, only to find that after your calculation it is too small and you must go back and re-calculate as you state in step 5 of your explaination.
Here is how I size my conductors.
Using your 60 amp/4 current-carrying conductor example:
Step 1: Compute the load at 125% of continuous, plus 100% of non-continuous load. (In this case all non-continuous). 60 amps.
Step 2: Check equipment ratings as per 110.14c. If you are certain that all the equipment is 75 degree rated, choose a conductor rated 60 amps from the 75 degree column. If not certain, choose the conductor from the 60 degree column. Write that conductor down. A #6 is selected from the 75 degree column for 60 amps. A #4 from the 60 degree column.
If there are no adjustment or temperature factors involved, the correct conductor size has been selected. If adjustment or correction factors are involved, go on to steps 3 and 4. Steps 3 and 4 are applied to the actual load (not 125% of continuous plus 100% non-continuous).
Step 3: Adjacent conductor adjustment. Merely divide the .8 adjacent conductor correction factor thats required for 4 current-carrying conductors in a raceway into 60 amps. 60 divided by .8 equals 75 amps.
Step 4: Ambient temperature correction. No (1.00) ambient temperature correction is required for your example.
You now only have to select a 75 amp rated conductor in the column that matches the temperature rating of the wire that you are using. For conductors in the 90 degree column, a #6 is rated 75 amps. If you were using 75 degree rated wire, #4 would be required for 75 amps.
Compare the conductor selected in steps 3 and 4 with the one selected in steps 1 and 2. The larger of the two is the correct size.